Audience in-wall shielded 10 gauge cable.
The cable IS NOT Listed for use as branch circuit power wiring.
NEC/ AHJ (Authority Having Jurisdiction) requires the branch circuit wiring shall be Listed by a recognized NRTL testing laboratory, example of an NRTL, UL.
NEC 110.2, 110.3 (C)
.
I have two dedicated outlets for my system using standard 12 gauge with short runs of about 15’ to the breaker box.
Pretty short runs... Any chance of voltage drop is slim to none.
Just curious, do you have any surge protection to protect your audio equipment? A Whole House Surge Protector at the electrical panel?
.
Thanks for the comment. Both lines are on the same leg of my box,
Best way to verify 100% is to check with a volt meter, multimeter.
If both dedicated branch circuits are fed from breakers on the same Line, leg.
Measure for voltage, from a hot contact of a duplex outlet, connected to one dedicated branch circuit, to a hot contact, on the other dedicated branch circuit duplex outlet. You should measure zero volts nominal.
IF you measure 240Vac nominal then the two branch circuits are not fed from the same Line, but rather are fed from Line 1 and Line 2.
.