Imagine the power cord to be some extension of the transformer’s primary in a power amp, and read up a bit on how tranformers are spec’d.
Brilliant! You’ve got it right! Thanks for posting.
Seems brilliant, but let’s scrutinize this analogy a bit. A 12 AWG power cable has about 0.00159 Ω/ft of DC resistance. Over 2 m, that works out to roughly 0.01 Ω. A typical 400 WPC high-current Class AB amplifier (60% efficiency) draws about 5.6 A, so the voltage drop across this resistance is V = IR = 0.056 V.
On the transformer side, a typical single-phase transformer has about 5% regulation, meaning the voltage drop at full load is around 120 V × 0.05 = 6 V. In comparison, the voltage drop due to the power cable resistance is only about 1% of the transformer’s own regulation.
This shows that the analogy does not hold up in practice—the cable’s effect is trivial relative to the transformer’s design limitations.
Still, I like the analogy.