I have an older house and my wiring is only 2 conductors. I have just yesterday ( weird coincidence ordered the 20 amp leviton unit from amazon ( got the orange one for a few bucks cheaper. I am wondering if I should crawl under the house and run a ground rod to the ground part of this outlet or just put a jump over to the neg side and be done?
Oh dear dark goddess of the undworld..... no!! 🤣
The correct thing to do is to use a GFCI outlet OR to have an electrician properly install a grounding electrode and bond it to the neutral at the service entrance. THEN and only then you run a ground to your outlets.
You don’t run a separate ground, and you sure as hell don’t tie your ground to the neutral anywhere else.
PS- Lacking a ground you can use GFCI for shock prevention when properly labelled, but surge protectors for the most part won’t work right.