Don’t hire a guy like this to install a whole house SPD, (Surge Protector Device.)
FLUSH mount Whole Home Surge Protector Install
Note, I didn’t say Electrician. Though I think he may play one in real life.
Final install is worthless as a Surge Protectror Device. It won’t protect anything, imo...
Most obvious no, no in the video... Never, ever, extend the leads of a Type 2 SPD. Look at all the wire he left in the right hand panel. The guy must have extended the SPD neutral and ground leads 4ft! WOW! Two hot wires at least 2ft! And in the left panel he left good size loop of wire.
/ /
Now this guy kept his SPD leads short. He could of made them even shorter without making any sharp bends. Inches matter... I would have twisted the leads together somewhat, all the way to the termination lugs.
How To Install A Whole House Surge Protector | TL Davis Electric & Design
See a problem with the installation?