Sounds like you might be thinking all the breakers on the left side of the electrical panel are on one leg, and all the breakers on the right side of the panel are on the other leg. That is not the case... The breakers on each side alternate from Line 1 leg and Line 2 leg down both sides of the panel. The wider breakers, two breakers with a single common handle, are for 240V loads. Single breakers are for 120V loads.
@jea48 , I was also thinking that the left side is one leg and that the right side was the other leg. So I guess that this means that the 240A breaker for my drier is using both legs?
And also: the way you explained that is that the top most breaker on the left side and the top most breaker on the right side are both on the same leg? (And from there on all the way down the legs alternate in pairs of breakers.) Am I understanding you correctly?