@spenav + 1
Type 1 SPD at the meter.
Type 2 UL Listed/Certified SPD at the main electrical panel.
If by chance the audio equipment is fed from a sub panel IEEE recommends a Type 2 SPD there as well.
I also have the Eaton CHSPT2ULTRA SPD.
Installation instructions ( Install the SPD as close to the incoming Power Lines, Legs, Main breaker, as possible to the 2 pole breaker the two Line SPD leads will connect to. The shorter the leads the better. Avoid sharp bends. Look at the photos in the link.
Another good Type 2 SPD is the Siemens FSPD 140KA.
Siemens FSPD140 140kA
Point of use Type 3 is also recommended by IEEE.
/ / /
@rpmpam
Mother Earth grounding is very important for the SPD to function as designed to protect from a near by lightning strike high voltage transients. The lower the Grounding Electrode, (a ground rod for example), to earth soil resistance the better. Simple OHMS LAW...
IEEE recommends 5 OHMS or less for commercial electrical services. NEC code says, if tested , 25 Ohms or less. (25 ohms is way to high for the SPD to divert the high voltage lightning transients fast to mother earth. (a lightning high voltage transient(s) lasts, is over, in less than a blink of an eye), Again simple OHMS LAW.) NEC says if the Grounding Electrode to soil resistance is greater than 25 ohms it shall be augmented by one additional electrode, driven ground rod. (NEC minimum size ground rod is 5/8" X 8ft). No further testing is required by NEC. A very good chance not by your electrical inspector either. Electrical contractors just have the electrician drive two rods, connected together and install a bare solid #6awg copper wire and connect it to the electrical service’s Service Entrance Neutral Conductor and both are bonded to the metal enclosure of the main service equipment, electrical panel. Service is grounded, meets NEC and any local electrical codes.
So what is your actual Grounding Electrode to soil resistance? I have never heard of a residential electrical contractor spending the money to test the resistance. Drive two 5/8" X 8ft ground rods in the earth and they are done. Move on to the next job and never look back...
In Florida, from reading what you said about the soil, the rod to soil resistance might measure 50 ohms, 100 ohms, or more ??? . What are the chances of adding an additional ground rod will lower the resistance to 25 ohms? Which is still to high for the SPD.
Something else, a low Grounding Electrode to soil resistance of 5 ohms or less will help do. In the event of a utility high voltage power line coming in contact with the low voltage power lines feeding your house.
(NOTE NO SPD will protect from a utility high voltage power Line coming into contact with your power Lines feeding your house event. IF the Grounding Electrode to earth soil resistance is low it will help drain the high voltage to the Earth. The Electrical Circuit? ... All them ground rods driven into earth. All are paths through the earth back to the Utility Company’s grounded high voltage power source.)
From what you said about the soil where you live I doubt driving addional ground rod(s) 8ft each in the earth and connecting them together to your existing Ground rod will do much for lowering the resistance. The only way to find out is to contact a reputable commercial Electrical Contractor in you area. Good chance he may not own the testing equipment required. He will have the phone number of a Power Quality Company he uses.
After the Power Quality Tech evaluates your situation he will give the Electrical Contractor his recommendations for a 5 ohms or less ground rod installation. (If, that’s what you or the Electrical contractor and or the Power Quality Tech recommends.)
My guess is one ground rod driven deeper into the earth at one location near the electrical service’s main service equipment.
Depth? Here I would use 5/8" X 10ft ground rods. The Power Quality Tech might tell me to drive 20ft into the earth and call him back to test the resistance. At that point I would probably respond it would be cheaper to drive three coupled 10ft rods in to the ground and then give the Tech a call to come and test the ground rod to soil resistance. 30ft deep may do the job and measure 5 ohms, or less. If not, add another 10ft rod. Check rod to soil resistance again.