@erik_squires said:
Supplemental ground rods must be bonded together with at least 6 gauge copper wire. Running a wire from a branch circuit is not ok.
That is correct for a Supplemental ground rod. Not required for a Supplementary ground rod. For a Supplementary ground rod NEC doesn’t require any size wire shall be used. ( Note: Years ago NEC changed Supplementary to Auxiliary because, for one, Electrical Inspectors (some?) used the code requirements for a Supplemental ground rod also for a Supplementary ground rod. Thus NEC changed the name from Supplementary to Auxiliary. (See my post above on
So the OP’s ground rod would meet NEC 250.54 code if the ground rod was connected to the wall outlet’s branch circuit EGC (Equipment Grounding Conductor.)
Auxiliary Grounding Electrodes [250.54], NEC 2023
https://www.youtube.com/watch?v=4a8Kh5aLCB0
I have said many times on this forum, Lightning loves them. Your audio equipment electronics, not so much...
Auxiliary Grounding Electrode NEC 250.54
Supplemental Electrode NEC 250.53(A)(2)