@ecat026 Said:
This is what NEC code calls for. Had to scroll too far down for to finally reach the correct answer. You can also replace the first receptacle on the circuit with the GFCI and attach the downstream receptacles to "load" and label them per above. This will ensure each receptacle on the circuit is protected by the single GFCI. Or place the GFCI solely on the receptacle in question.
FYI, 2020 NEC 406.4 (D) (2) (a) says an old two wire receptacle can be replaced with a new 2 wire receptacle when there is not an equipment ground present.
Would a GFCI outlet be better for his situation feeding his audio equipment? Yes... If the box is deep enough... IMO a new 20A dedicated branch circuit would be better. My bet the OP will hear a difference, for the better.
Back in the old days some of the steel boxes used for wall outlets may not be deep enough for the installation of a GFCI duplex receptacle. (He has 4 cloth covered rubber conductors in the box as well.) The electrician he hires will check the box for fit. I am sure the electrician will know what he can do.
FWIW...
There are other options to add GFCI protection to the 2 wire convenience outlet branch circuit. One, is to install a GFCI breaker in the electrical panel. (providing the branch circuit is not part of a multiwire branch circuit.) That would also allow a 3 wire grounding type receptacle to be installed for his audio system. (Label would be required on the outlet cover plate.) Just a guess, more than likely all the duplex outlets on the 2 wire branch circuit have 3 wire grounding type outlets installed on the 2 wire circuit. Just a guess there may be some ceiling lighting on the circuit as well.
What the OP should not do himself is mess with the old branch circuit wiring. Especially if the insulation on the wires is old cloth covered rubber.
Best regards,
Jim