lowrider57 OP3,544 posts
02-26-2020
4:06pm
To power up the system, I turn on the Equi=Core, then the panel breaker trips immediately. I used to repeat this procedure but the panel tripped every time I turned the EQ on.
@lowrider57
That tells me the branch circuit wiring is fine. The 20 amp breaker didn’t trip until you turned on the EQ unit using the ON/OFF switch.
It sounds like you have been tripping and resetting the circuit breaker a whole bunch of times. Not just a few times. It sounds like it was the magnetic trip device in the breaker that was tripping the breaker open. I am not sure the magnetic trip device weakens with several repeated very high inrush current and or from a ground fault or short circuit event/s. I do know the overload thermal trip device does though. You weren’t tripping the breaker on overload, imo..... You said the breaker would trip immediately.
If the secondary of the transformer was not loaded, (say by at least 50% or more), from a cold start up the primary winding would not draw all that much inrush current. No where near enough current to trip a 20 amp breaker...
Just a stab in the dark I would say the transformer is the culprit. I would also guess what ever is going on it has been progressively getting worse. I would not try use it until you have it looked at.
As for the 20 amp breaker in the electrical electrical sub panel.
Because of all times the breaker has been tripped, and then you trying to close the breaker under a load. At a very high current load I might add. Possibly at a hundred amps or more, the contacts in the breaker have to be really burnt and pitted.
Jmho, I think you are darn lucky the contacts did not weld themselves together.
Side note:
I should mention depending on the breaker manufacture the 20 amp breaker may be a SWD rated breaker. An SWD rated breaker is rated to be used as a switch to turn on and off florescent lighting like you see in a store like Target and Walmart. (Now no doubt LED)... The calculated maximum continuous connected load for a 20 amp circuit breaker is 16 amps. 80% of 20 amps. You were switching a load of maybe 100 amps or more.....
Jim