bought Audio Magic's Sorcerer 4D cable in bulk to make separate runs from my breaker box directly to the components. When I opened the ends of the Audio Magic cable there two big conductor lines separately insulated inside the foil shield. Each insulated bundle has 4 wires inside and should be around 6-8AWG in total. But to my suprise, there wasn't any ground wire visible, except a single run of a 20AWG insulated wire. I asked about it to Cable Company where I purchased the cable and they asked to Audio magic about this and they confirmed that small gauge wire is to be used as Ground. Somehow I'm a bit worried because I've always known and seen Ground wires to be around the same gauge of current carrying wires. Is this OK to use?
muratc

Showing 1 response by gs5556

Wire that's rated for 15-amps must have a No. 14 ground and wire rated for 20-amps must have a No. 12 ground. Eldartford, even though you are correct that no current flows through the ground, it's purpose is to act as a secondary path back to the panel in the event of a fault. This is so that the circuit breaker can trip, protecting the faulted circuit. If you cannot reset a breaker, then you have a fault.

I don't know how you determined that the size is 20AWG. Even low voltage control wires are a minimum of 18AWG. Now, if the cable has a metal jacket, then that jacket is the ground and is perfectly ok. The thin wire, in this particular case, would be a bonding wire which completes the connection to the jacket ground. If the jacket is non-metallic, then anything less than 14 wire is not safe and in most jurisdictions illegal.

Check with an electrician or the local building department to be sure.