Dedicated line questions...


Did a search, but can’t come up with a good answer. I am considering the install of a dedicated line. The general consensus is a 20amp circuit. How does this rectify with a full system designed around 15amp components/cords. I already have PS audio receptacles, and have upgraded/cleaned up all the other outlets on the current circuit, but it is still noisy. Would installing a 20amp circuit require a refit of gear or just 15-20 amp power cords? I don’t run big mono’s and really only need one line. Would a dedicated 15 suffice?  Yeah, fairly clueless in this realm.
geof3

Showing 1 response by jea48

spatialking323 posts

01-08-2021
7:09pm

I have read through this post and I noticed some folks here use both lines from the distribution panel. That is, line 1, line 2, neutral, and earth, such as would be wired when using the Southwire 10 awg, 3 wire. Since line 1 and line 2 are opposite in phase for North America (and anywhere else where split phase lines are used) that means hum is more likely to occur since the outlets are no longer identical polarization.

@spatialking
I suggest you reread the thread again. No one mentions using both Lines, legs, (therein a 120/240V multiwire branch circuit), to feed a single dedicated 120V branch circuit.

I think you misunderstood what @gs5556 meant when he recommended using 10-3 with ground Romex for a 120V dedicated branch circuit.

FWIW, 3 conductor with ground NM sheathed cable (Romex is a Trade Name of Southwire) is not designed/manufactured only for use for 120/240V multiwire branch circuits. 3 conductor with ground is also used for 3 way switching of lighting as well as split duplex receptacle(s) switching for table lamps. Top receptacle of duplex is hot all the time, bottom receptacle is switched by a wall switch.
.