Dracule1,
Which ever external mounted SPD you go with the unit protects best when the wire leads from the SPD are as short as possible.
If possible the breaker used to connect the SPD to the bus of the electrical panel should be installed as close as possible to the load side of the main breaker as well as the neutral/ground bus bar. Inches matter!
Sharp bending of the SPD wire leads must be avoided.
As for the Eaton CHSPT2ULTRA you will notice the manufacture recommends a 2 pole 50 amp breaker be used for connecting the the SPD to the electrical panel bus.
More reading material.
http://www.erico.com/public/library/fep/technotes/tncr019.pdf
.