I agree on a whole house Type 2 SPD
I use Tripp-Lite Ultra Type 3 point of use SPDs on the PC computer and Home theater system. Various other LED TVs I use Tripp-Lite Type 3 SPD power strips.
(FYI,The branch circuit wiring length must be a minimum of 30ft to use a type 3 point of use SPD. That is now a requirement in the 2023 NEC. It has been a UL requirement for at least a few years. Impedance and inductance matters in the branch circuit wiring when using a plug in Type 3 point of use SPD.)
The whole house Type 2 SPD must be installed per best practices.
The majority of high voltage transient surges in a home are caused by electrical appliances and electrical equipment found in the home.
For lightning protection a low resistance Grounding Electrode system is also needed. IEEE recommends 5 ohms or less for commercial and industrial facilities.
NEC just says if the electrode to soil resistance "is measured" it shall be 25 ohms or less. Way to high... The lower the grounding electrode to soil resistance the quicker the high voltage lightning transient is diverted to Mother Earth. Simple Ohms Law.
.