Do you know if the Electrician used the red #10 conductor for the safety EGC, (Equipment Grounding Conductor), for each dedicated circuit?
If you are not sure would you feel safe checking at least one of the dedicated branch circuits? You can check just one of the wall outlets. Pick the easiest one to get to.Turn off the breaker that feeds the outlet. Verify 100% the outlet is dead. Plug any item into the outlet to verify it is dead.
You will have to remove the outlet cover plate. Then remove the two 6/32 machine screws that hold the duplex receptacle to the wall box. Pull the outlet from the box just enough to look inside the box. You may need a flash light. Is the box steel or plastic?
Look for the red #10 wire/conductor. The electrician more than likely taped it green using green marking tape.
IF the box is made of steel...
You should see the Red wire, (green taped with green marking tape), has two pigtails attracted/connected to it with an insulated wire connector.
One pigtail fastens to the back of the steel box with a green color 10/32 machine screw.
The other green pigtail fastens to the green color equipment grounding screw on the duplex receptacle outlet. (Good chance the green insulated pigtails are #12 AWG copper wire manufactured grounding pigtails.
IF the wall outlet box is plastic, the #10 stranded red, taped green, wire/conductor is fastened directly to the equipment ground screw on the duplex receptacle. If that is the way he did it, he more than likely used a crimp on spade lug. He also could of used a manufactured #12 green grounding pigtail and jointed/connected it to the #10 stranded ground wire. The green pigtail fastens to the duplex outlet green equipment ground screw.
Jim