I doubt the PS Audio regenerator would handle the load of two Audio Research REF 160M mono block amplifiers.
Maximum continuous load, 2000VA
2000VA / 120Vac = 16.67 amps max
Maximum peak load, 3600VA
Peak is fast quick draws of current. Lasting how long? Millisecond duration?
3600VA / 120Vac = 30 amps max.
.
ARC TECHNICAL SPECIFICATIONS
Power output:
140 watts continuous from 20Hz to 20kHz. 1kHz total harmonic distortion typically 1% at 140 watts, below 0.04% at 1 watt. (Note that actual power output is dependent upon both line voltage and “condition” i.e.: if power line has high distortion, maximum power will be affected adversely, although from a listening standpoint this is not critical)
.
|
Power Requirements per Monoblock |
105-130VAC 60Hz (210-250VAC 50Hz) 400 watts at rated output, 700 watts maximum, |
.
I am pretty sure the 105-130VAC line voltage does not mean the amp will function properly if the AC line voltage is not steady. I doubt the high DC voltage section of the power supply has voltage regulators.???
Playing music with high dynamic passages at a moderated to high volume level could very well reach 700watts X 2, maybe more. Does the 700 watts take into account fast, quick, short high dynamic passages of music being played?
.
enter,
Wire Size.
Material of Conduit.
Distance.
Load Current.
Enter distance of branch circuit wiring from electrical panel to wall outlet. (Distance is up, down, over, and back. Not a distance of strait as a Crow flies.)
Enter load current. (Continuous). Press Calculate.
Press Clear.
Enter estimated dynamic load current, ampere, peaks.
Press Enter
Write down results.
Next, for wire size, enter #10AWG. Press Enter.
.
.
Food for thought:
2x200W amp might take from mains close to 1kW during peaks. The problem is that peak supply current won’t be expected 8A, but rather close to 40A. It is because current is drawn only for very short time (millisecond pulse) at the peak of full wave rectified sinewave. It applies to most of LPS. Power delivered with such short pulses not only creates larger voltage drops in house wiring, but also heat-up amp’s power transformer, that has to be oversized (higher copper losses and higher core losses for eddy currents and hysteresis).