Running supply voltage of 60/60 - Vs - 120/Neutral


With the power system im running now, it supplys power at 60 volts and 60 volts each leg, Versus the nominal 120 volt and neautral, im curious as to what the benifits and problems that this may cause for audio equipment, with running no neutral, i get this off of the isolation transformer, as part af a large power system with battery backup to insure than nothing frys in the event of surges and electrical storms, could this possibly cause a better "balance" and maybee increas audio quality? it's definatly a safer system as you would not get shocked unless you touched both legs at the same time.
archangelluke
The APC is the battery backup, 7500 va model, it operates at 208/240 1 ph, i have it set to 240 in and out, and have to use a TX on the output to achieve 120, as you cannot split the 240 on the output of the APC of course, the transformer is rated at 2kva or 2,000 Va, at the current tap im running, the sunfire does humm at idle, but less than say 5db, so its just barly noticable, but lowd enough to keep it from going to stanby on the auto power off, when i plug it directly into the wall the humm seams less, and enough to let it go to standby when not in use, and of course the noise test is done without the low level input connected, and connected sounds the same.
but i am bonding the ground to everything, from the chasis, to the transformer casing, to the outlet it self on both pri and sec sides, and did run a #1Odd welding cable to bond directly to grounding rod, and this still made no diff, i am moving next week to an apt. and will re-evaluate the system then, i will then do tests to see if this setup does endeed kill the dynamics of the systms sound, as that is what i heard you get with a lot of power filters, as right now this is basically what the service goes through before it hits my equipment:

240V main service into home into primary filter which consists of 1 large inductor filter per phase, then a high energy surge protector, then a small filter cap to ground per phase, after that it runs though the main panel to a dedicated 30 amp 240v circuit upstairs into the "APC" (battery backup) in that it filters the power again, with numerous Torrid filters and filter caps, then it drives the power through SCR's to process the frequency and voltage, (no normal bypass as some battery backups do) then it leavs the APC and goes into my home brew dist block, (the large grey thing next to the apc in the pictures i have up)there it runs though the isolation/step down transformer, then it pases through the EMI/RFI filter (both legs), then to the outlet. and meanwhile the same ground on everything, everywhere.
The input has been config for 240v"

Yes #2 & #3 tied together With the 240V supply connected to terms #1 & #4.

That is correct.
Post removed 
Im in independence, Missouri, about 30 miles east of KC.

I had never thought to gound the #5 terminal,but maybee the #0 or the 0Volt tap,i figured it would short the primary, but i will fuse it low and try it, then that would eliminate the 60/60. but i do run the power after the transformer through the EMI/RFI filter, before it hits the outlet.

And this is just for the sub, i still have one other dual coil transformer im using for the rest of the equipment, but the output on both seam to be a little high, around 126 at low to no load, im not sure what the tube stuff likes best, im sure the sub wont mind.
I have a currently unused variac installed and "was" using it to drop output to around 115, for the amp,tv,xbox etc.