New Dedicated Line - Almost No improvement


Hello,

Newbie here and electrical idiot. Just moved to a new to us house in Tampa. Before we moved in I had an electrician put in a dedicated line (has it's own breaker switch) which is 10 gauge and two Furutech GTX-D outlets - Rhodium.

When I hooked up the EMI meter in my old house, which didn't have a dedicated line, the reading was usually around 26 or so IIRC. At the new house the outlets are 89 usually and the dedicated line is usually around 82 - so not much help for the cost of the "project" and pretty noisy.

Also, when the ac /hvac is running the meter reads about 100 points higher (!) for both the regular outlets and the dedicated Furutechs. Not good.

Thoughts? Does the dedicated line need it's own breaker box? 

I'm also considering a line conditioner but wanted to see what could be done here. Thanks.

laynes

@jea48 , while I agree in principle that an earth ground connection is generally not the cause of noise, it is not always not the cause, and when one considers emitted EMI, it can be critical. The earth ground connection (in theory) holds the metal in the equipment, cable shields, etc. to the same potential as earth, but we can call it a ground plane. Now as noted, that connection is more than just cable resistance, it is also impedance. If you remove the earth ground connection, then all the metal floats, and it floats in comparison to earth ground, which means you have a capacitor to earth ground and a "new" path for EMI that you would not have if connected to earth ground. This will never be an issue at analog audio frequencies, but it can be an issue at higher frequencies even with the higher impedance to earth ground.

 

You know what is really foolish? Those ground boxes filled with dirt that don't connect to anything.

@lowrider57   I think the grounding issue has assumed a life of its own, per the above comments.  I used 1/2 or 5/8 solid copper pipe (not an iron/copper grounding rod., 6 feet long. We drilled straight down, hammered the rod in and then filled the hole with a high-clay content soil. Was told this clay compound would help with grounding and conductivity. I was skeptical, but for the additional $15, I wasn't going to argue that point.  

My point really is there are many factors to consider with stable, clean power to the audio room. I didn't want to inadvertently omit one thing that might render all the other work wasted.  And as pointed out, we are still at the mercy of the grid.

Post removed 

I used 1/2 or 5/8 solid copper pipe (not an iron/copper grounding rod., 6 feet long. We drilled straight down, hammered the rod in and then filled the hole with a high-clay content soil.

Is the grounding electrode only 6 ft deep in the earth? If so unless it rains a lot and soil moisture content is high you have a poor high resistance ground, imo...

I hope this is not the only earth connection for your electrical service. The System Ground, Grounding Electrode System, is mainly for lightning protection. It also somewhat protects the electrical service from a high voltage fault of the high voltage power line onto the low voltage secondary side of the power transformer from entering your house. The lower the resistance of the Grounding Electrode System the better. IEEE recommends 5 ohms or less.

Example of grounding electrode depths in the earth. (Climate Change and droughts would make things worse)

http://www.cpccorp.com/deep.htm

https://droughtmonitor.unl.edu/

A practical guide to earth resistance testing