Should I redo the AC power in my house?


I was inspired by the Michael Fremmer YouTube about how he went to great lenghts to address the power in his home. Also was urged to do so by Mike Lavigne. Thanks Mike.

Fremmer and Lavigne are thrilled with the difference it makes in SQ. Perhaps comparable to getting the next level up on all components. Mike referred me to the consultant both he and Fremmer used-Rex Hungerford of King Rex Electric.

I would not go to the lenghts of those fellows but still would do a lot. The whole job should run about $4-5K. I started this current quest interested in grounding but Mike L and Rex both highly recommended I go the full boat.

 

 

mglik

Showing 4 responses by jea48

@erik_squires

jea48 said:

It does nothing for the sound of an audio system.

@erik_squires response:

I dont’ think this is proven, or even well investigated. If you wanted to show this, you’d have testing done with say, an elevated ground and measurements of noise on the ground wire in a home, and then also do some testing to see how well this noise can or cannot couple to audio systems.

Fact!
Mother earth does not possess some magical mystical power that sucks nasties from an audio system. If anything it can introduce noise onto the AC mains.


Grounding Myths

"Electromagnetic Compatibility Engineering" by Henry Ott

3.1.7 Grounding Myths

More myths exist relating to the field of grounding than any other area of electrical engineering. The more common of these are as follows:

1. The earth is a low-impedance path for ground current. False, the impedance of the earth is orders of magnitude greater than the impedance of a copper conductor.

2. The earth is an equipotential. False, this is clearly not true by the result of (1 above).

3. The impedance of a conductor is determined by its resistance. False, what happened to the concept of inductive reactance?

4. To operate with low noise, a circuit or system must be connected to an earth ground. False, because airplanes, satellites, cars and battery powered laptop computers all operate fine without a ground connection. As a mater of fact, an earth ground is more likely to be the cause of noise problem. More electronic system noise problems are resolved by removing (or isolating) a circuit from earth ground than by connecting it to earth ground.

5. To reduce noise, an electronic system should be connected to a separate “quiet ground” by using a separate, isolated ground rod. False, in addition to being untrue, this approach is dangerous and violates the requirements of the NEC (electrical code/rules).

6. An earth ground is unidirectional, with current only flowing into the ground. False, because current must flow in loops, any current that flows into the ground must also flow out of the ground somewhere else.

7. An isolated AC power receptacle is not grounded. False, the term “isolated” refers only to the method by which a receptacle is grounded, not if it is grounded.

8. A system designer can name ground conductors by the type of the current that they should carry (i.e., signal, power, lightning, digital, analog, quiet, noisy, etc.), and the electrons will comply and only flow in the appropriately designated conductors. Obviously false."

Henry W. Ott

 

Who is Henry Ott?
http://www.hottconsultants.com/bio.html

 

The best way to introduce noise as well as a difference of potential, voltage, onto the chassis of audio equipment is by using an isolated dedicated driven earth ground rod.

(isolated dedicated driven earth ground rod? An Earthed grounding electrode that is not connected to the electrical service main grounding system. Therein Grounding Electrode System.)

When an isolated dedicated ground rod is not connected the electrical service Grounding Electrode System a difference of potential will exist between the two earth connected grounding electrodes. Always.

A year ago or so I got into a pissing contest with an EE on another forum. So for a test to prove I was right I drove a 5/8" x 8ft ground rod in the rock garden outdoors by my 2ch audio room. The rod is about 70ft to 80ft from the electrical service’s three 5/8" x 10ft driven ground rods. Also incoming water main piping is 1" copper buried in the earth probably at least 6ft that is part of the electrical service grounding electrode system.

I just did a quick measurement between the two isolated grounding electrodes and I measured 216 - 220 AC mV.

FWIW... The year or so ago test I connected the hot 120V AC conductor of a 20 amp circuit to the isolated dedicated ground rod to prove the 20A breaker would not trip open. And as I already knew the breaker did not trip.

 

Fremer Installed a new electrical service replacing the old, in bad shape, outdated one. That in itself would make a big difference. Just look at the old meter socket in the video. The old aluminum wiring connections were corroded. More than likely the aluminum wire connections were not tight either. Poor corroded connections equals excessive harmonic distortion. Excessive harmonic distortion equals noise on the AC mains wiring.

Add to that all the old utility power wiring to new service wiring terminations at the overhead weatherhead were replaced. That can make a big difference...

I did take note of the earth grounding connections methods used in the video. That’s probably the first time I have ever seen Cadweld (Exothermic Welding) terminations used for the connections of the grounding electrode conductor to the earth driven grounding electrode, ground rod(s). That ain’t cheap!

FWIW the main purpose of the electrical service to earth connection is for lightning protection. It does nothing for the sound of an audio system.

 

 

 

 

.

 

 

Fremer’s new electrical service was wired to the current code for the AHJ, (Authority Having Jurisdiction), in his area. The wiring and wiring methods used can exceed the AHJ requirements/standards as long as the wiring used and wiring methods used meet the minimum AHJ standards.

 

AS I have said many times... Code is bare minimum...

With that said, bare minimum Still has to be met...

Example, NO ISOLATED DEDICATED GROUND ROD(s) All grounds rods shall connect to the main grounding system of the electrical service.

 

 

Quote:

National Electrical Code 90.1 Purpose:

(A) Practical Safeguarding. The purpose of this Code is the practical safeguarding of persons and property from hazards arising from the use of electricity. This Code is not intended as a design specification or an instruction manual for untrained persons.

(B) Adequacy. This Code contains provisions that are considered necessary for safety. Compliance therewith and proper maintenance result in an installation that is essentially free from hazard but not necessarily efficient, convenient, or adequate for good service or future expansion of electrical use.

Informational Note: Hazards often occur because of overloading of wiring systems by methods or usage not in conformity with this Code. This occurs because initial wiring did not provide for increases in the use of electricity. An initial adequate installation and reasonable provisions for system changes provide for future increases in the use of electricity.

’’FWIW the main purpose of the electrical service to earth connection is for lightning protection.It does nothing for the sound of an audio system.’’

Agreed!

JUUP!

The ground that can have an effect on the sound of an audio system is EGC (Equipment Grounding Conductor). Therein, Ground loop hum. AC noise.

The EGC, when used, is connected directly to the chassis of the audio equipment. Also connected to the chassis is the power supply B - and signal ground. (A well designed piece of equipment does not have the B - and signal ground connected directly to the chassis, when an EGC is used. Usually it is in series with a low ohm resistor or some other series component device.

A good read about the affect of the EGC on audio equipment.

Read pages 16 thru 36. Then go to page 196 and so on if interrested.