Grounding Rod


Where should I connect the grounding rod to? I am planning to put a 8' grounding rod. But should I connect it to the ground of the AC outlet? I have a dedicated line and I can wire the grounding rod to the ground contact of the AC outlet. Or should I connect it to the equipment?

I have read a few theory on the net. I'd like to know what works best in practice.
vett93
To enable a breaker to trip, fault current has to flow back to the source (the power company transformer) via the incoming neutral, not the earth. The impedance of the earth by itself is too high. The main purpose of the earth ground is for lightning protection and to stabilize the supply voltage. IMO the use of the term "ground" when referring to the protection against fault current is a misnomer, because in reality, it is the return of this fault current via the service neutral that affords the protection.

http://img.villagephotos.com/p/2003-5/191557/circuit%20%20load.JPG

http://img.villagephotos.com/p/2003-5/191557/ground_fault.JPG
Gbart
I'm pretty sure the subject "ground fault protection" was never addressed before in this thread concerning where to place the ground rod, either on the equipment or on the outlet, nor am I sure it applies. Regardless, the subject "ground fault protection" should be explained further.
Please continue...
Jea48,
Thank you. Very illustrative explanation as to why it would be a such a bad idea to have an outlet connected to it's own ground rod. That's a ground fault easy to understand. Some folks may poo-poo the NEC rules, but they're in place to guard against those "perfect storm" situations and should not be considered subject to interpretation. Thanks again.
Thanks all for the comments. I have decided not to add the grounding rod. But the quest for reducing noises continues...