I am not sure how far back the NEC allowed metal conduit to be used as an equipment grounding conductor. The earliest NEC I have is 1971.
1971 NEC 250.91 (B). Types of equipment grounding conductors.
(1) Copper conductor or other corrosion-resistant conductor ... more wording solid, stranded ect... Nothing said specifically about the use of Aluminum conductor.
(2) Rigid Metal Conduit
(3) Electrical Metallic Tubing (EMT)
(4) Flexible metal conduit approved for the purpose, .......
(5) Armor of Type AC metal-clad cable
(6) The sheath of Type MI cable
(7) The sheath of Type ALS cable
(8) other ......
/ / / /
From earlier post:
Yes you can. NEC 250.118 (2) (3) (4)
The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more or a combination of the following:
- A copper, aluminum, or copper-clad aluminum conductor. This conductor shall be solid or stranded; insulated, covered, or bare; and in the form of a wire or a busbar of any shape.
- Rigid metal conduit.
- Intermediate metal conduit.
- Electrical metallic tubing.
- Listed flexible metal conduit meeting all the following conditions:
This was not a complete list of all the types of equipment grounding conductors allowed. I just stopped at #5.....
.