Edit:
(The white insulated neutral conductor, the green insulated equipment grounding conductor, and the black insulated Hot conductor.)
Look closely at the two pictures in the Link provided. Look for the cable with a, white, green, and black, insulated conductors. Look closely for the bare aluminum bonding strip.
http://www.afcweb.com/ac-hcf-armored-cables/hcf-lite-aluminum-health-care-facilities-cable/
Click onto "specifications" for data sheet.
Jim
.
Like MC, it contains an additional grounding conductor, although with this type of cable it is permissible to use the metal jacket as the safety grounding conductor, as required with isolated ground installations.Not exactly... The armor alone is not considered an effective equipment grounding conductor. There is a (bare aluminum bonding strip) that runs straight along side the three tightly spiral twisted insulated conductors.
(The white insulated neutral conductor, the green insulated equipment grounding conductor, and the black insulated Hot conductor.)
Look closely at the two pictures in the Link provided. Look for the cable with a, white, green, and black, insulated conductors. Look closely for the bare aluminum bonding strip.
http://www.afcweb.com/ac-hcf-armored-cables/hcf-lite-aluminum-health-care-facilities-cable/
Click onto "specifications" for data sheet.
Jim
.