Running 2 dedicated lines in my dedicated room


Hi guys need your opinion on this, im running 2 20A dedicated lines for my audio room. The pathway for these 2 lines are the same from the subpanel to my room but it differs once they are running over the ceiling in my room. The cables are resting on the bracings of my ceiling which will then be covered. 
One outlet will be placed over the left corner  and the other will be at the right corner of my front wall. Since they follow a different pathway in my room there's some discrepancy in length to the outlet for both lines.
My worry is will this be an issue due to the difference in cable length especially with the grounding cable? I did a measurement and the discrepency between both the cable length will be around 4.5-5ft. I'm not sure if that amount of difference will cause any issues.
Please do advise would love to hear your opinions. I have not covered the ceiling yet so I'm able to reroute them.
128x128tjbhuler

Showing 1 response by lak

If I understand your question correctly you want to know if the AC wiring length makes a difference, one will be 4.5’ to 5’ longer than the other.
Should not make any difference at all.
I’d be more concern if you were passing over some other type of a cable or dimmer that would possibly pick up some type of interference.

Out of curiosity; what type of wiring and what gauge wire are you planning on using?