Running 2 dedicated lines in my dedicated room


Hi guys need your opinion on this, im running 2 20A dedicated lines for my audio room. The pathway for these 2 lines are the same from the subpanel to my room but it differs once they are running over the ceiling in my room. The cables are resting on the bracings of my ceiling which will then be covered. 
One outlet will be placed over the left corner  and the other will be at the right corner of my front wall. Since they follow a different pathway in my room there's some discrepancy in length to the outlet for both lines.
My worry is will this be an issue due to the difference in cable length especially with the grounding cable? I did a measurement and the discrepency between both the cable length will be around 4.5-5ft. I'm not sure if that amount of difference will cause any issues.
Please do advise would love to hear your opinions. I have not covered the ceiling yet so I'm able to reroute them.
128x128tjbhuler

Showing 2 responses by giantsalami

I recently added 4 outlets, 6 circuits, for my system. two of the runs I ran 12-3 insted of 12-2 and seperated the jumper between the top and bottom outlets. ( one outlet, 2 circuits) I should be prepared for any future upgrades. Just an idea while you are running the romex.