I tried to post this yesterday but it didn't make it to the forum, so if it gets posted twice, that is why. I must concur with Carl109 as to the quality and efficacy of a safety ground connection made by the shield of an IC. I completely agree with him that this type of connection is likely not capable of carrying the fault current necessary for protection. Additionally, you run the risk of too high of an impedence to ground to reach the current needed to trip the breaker due to a hot chassis. Since the chassis of the equipment sitting next to the source does have a low impedence path to ground, touching both boxes at the same time could prove unhealthy. These problems don't occur when you ensure electrical safety via the designed method. I strongly recommend against defeating the intended safety ground and do not endorse relying on a ground provided by an IC to protect against fault currents. Besides, there is no good reason to do this. Solving the problem correctly is possible without creating any hazard.