I live in an apartment building that's relatively new (built in 1993). There are no visible power lines attached to the building, which leads me to believe the power lines are underground. The building has a dedicated line for air conditioners. I know very little about power outlets, wiring, amperes, etc. All I know it's 115 volts. Here's my question. I will be replacing my tube integrated power amp with tube monoblocks producing at least 150 watts per channel and a tubed preamp. I have seen occasionally discussions about the demand on the power line electronic equipment makes and parameters for dedicated lines and such. Should I worry about blowing fuses or overloading the power line with my new amplification? My gf and I triggered circuit breakers a few times in the past by using hair dryers simultaneously in our respective bathrooms, but once we stopped that practice, no other mishaps occurred. I have a basic power conditioner with 4 outlets, but that's about it. With my less than rudimentary knowledge of power delivery, I wouldn't even know where to start to answer my question so I thought I'd start here. Thank you for any advice.
actusreus

Showing 3 responses by jea48

Actusreus,

Easy as PIE....

P = I x E

p = power, watts, Va.

I = current, amps.

E = volts

To find (I) divide (P) by (E).

A 15 amp circuit should not be loaded more than 80% continuous load. 12 amps.... Or 1440 watts/Va....
It appears the lights in the apartment (judging from the list, this includes the power outlets), have a circuit with two separate breakers, each stating 15 on them. Does this mean there are actually two circuits of 15 amps each?
03-07-11: Actusreus
Actusreus,

Are you sure the building was built in 1993?
You should have a bare minimum of (2) 120V 20 amp branch circuits for the kitchen and at least (1) 120V branch circuit GFI protected for the bath room/s.

What you described is more representative of the 1960s and earlier....