Just for every ones information.
NEC 2011
Article 210.6 (A)
Occupancy Limitation. In dwelling units, and similar occupancies, the voltage shall not exceed 120 volts, nominal, between conductors that supply,
(2) Cord-and-plug loads 1440 Va, nominal, or less or less than 1/4 HP.
Fluffers,
It's a CDP.... Power consumption is next to nothing. JMO buy a small step-up transformer.
Also worth mentioning the 230V CDP was designed to be fed from a 230V AC grounded power system. A hot, (the ungrounded conductor), and a neutral, (the grounded conductor).
Good chance only one line, the hot conductor is fused inside the CDP.
Good chance the power switch is a single pole and only breaks one line, the hot conductor.
.
NEC 2011
Article 210.6 (A)
Occupancy Limitation. In dwelling units, and similar occupancies, the voltage shall not exceed 120 volts, nominal, between conductors that supply,
(2) Cord-and-plug loads 1440 Va, nominal, or less or less than 1/4 HP.
Fluffers,
It's a CDP.... Power consumption is next to nothing. JMO buy a small step-up transformer.
Also worth mentioning the 230V CDP was designed to be fed from a 230V AC grounded power system. A hot, (the ungrounded conductor), and a neutral, (the grounded conductor).
Good chance only one line, the hot conductor is fused inside the CDP.
Good chance the power switch is a single pole and only breaks one line, the hot conductor.
.